The cooling loads for a building are: RSH = 100 kW (Room sensible heat) RLH = 25 kW (Room latent heat) OASH = 10 kW (Outside air sensible heat) OALH = 10 kW (Outside air latent heat) The bypass factor of the cooling coil is 0.15. What are the values of the room sensible heat factor and external sensible heat factor respectively? |
| A. | 0.72 and 0.8 |
| B. | 0.8 and 0.79 |
| C. | 0.79 and 0.8 |
| D. | 0.79 and 0.72 |
| Answer» C. 0.79 and 0.8 | |