In a power system with negligible resistance, the fault current at a point is 8.00 p.u. The series reactance to be included at the fault point to limit the short-circuit current to 5.00 p.u. is ______p.u. |
| A. | 3000 |
| B. | 3.000 |
| C. | 0.300 |
| D. | 30.00 |
| Answer» C. 0.300 | |